hurk27
Senior Member
- Location
- Portage, Indiana NEC: 2008
We have a New AHJ in a small town we have been doing work in for a while. He keeps insisting that there has to be a grounding busbar installed anytime N/M type wireing is used because of artical 408.20. He is not red taging us yet as he is not sure about it ether but has asked me to provide a explaination as to why 408.20 does not have to be followed. I have never come accross this question before and after reading it I can see his dilima. But I think the anser is in the last paragraph of the artical (in bold):
I also brought up the requirment that grounding conductors and gounded conductors are only required to be kept seperate when the service disconect is located ahead of this panel. But he seems to understand this and said it wasn't about keeping the wires seperate, it was about what 408.20 was requiring. But I need to reply to him soon before he starts beliving this and starts red tagging.
Any help on how to explain it will help.
Thanks Wayne
Is there anything else that I can point out to allow him to understand this?Grounding conductors shall not be connected to a terminal bar provided for grounded conductors (may be a neutral) unless the bar is identified for the purpose and is located where interconnection between equipment grounding conductors and grounded circuit conductors is permitted or required by Article 250.
I also brought up the requirment that grounding conductors and gounded conductors are only required to be kept seperate when the service disconect is located ahead of this panel. But he seems to understand this and said it wasn't about keeping the wires seperate, it was about what 408.20 was requiring. But I need to reply to him soon before he starts beliving this and starts red tagging.
Any help on how to explain it will help.
Thanks Wayne