Its been a while since I had to do a calculation lately
Checking this neutral calculation for a feeder. These guys are putting in an expresso stand with some extra cooking equipment.
They have
2 120v 7.5a grinders 1800va
1 120v 2000watt water heater
2 120v duplex receptacles 360va
208v 25a espresso 5200va
208v 25a protein machine 5200va
208v and 3744va other machine (do not know what its called LoL)
I got about 55amps total just for the feed, neutral amps I guess can be about 35 amps from the 120v loads. Haven't checked the other 'unknown machine' to see if it had any other neutral loads
Their pulling a smaller neutral for the length about 105 to 110 feet. It was my understanding that their are no neutral reductions allowed for this feeder?
Did I miss something?