Neutral calculation

Status
Not open for further replies.

ciupol

Member
Location
Fargo, ND
Have a question about calculating neutral load for the service. In example D1(a) in Annex D in the section for neutral load calculation dryer is included in the calculation (at 70%). In the description for this example it is stated that dryer is a 240V equipment. Why do we have to include dryer in neutral calculation? I thought that 240V loads do not generate neutral current.
 
A true 240V load does not put any load on the neutral. (In a normal residential system, that is.)

But most driers are 120/240V devices. I would expect only a small neutral load for the 120V motor and controls, but perhaps some driers have high 120V loading, say for low temperature operation.

-Jon
 
Thanks for the answer.
One additional question though. So how can one know which loads should be included in neutral calculation? Should I always include all loads, even those marked 240V in the calculation?
 
Thanks for the answer.
One additional question though. So how can one know which loads should be included in neutral calculation? Should I always include all loads, even those marked 240V in the calculation?
Only 240V 1? 3-wire equipment, i.e. 120/240V. Cooking appliances, clothes dryers are the typical residential loads; some HVAC equipment...

No 240V 1? 2-wire equipment.
 