Neutral carried to disconnecting means?

Status
Not open for further replies.
I coulda swore that I saw a code stating that all disconnects are required to have a neutral pulled to them weather the neutral is used or not.

I cant find that code anymore and the question has rissen in our shop. Can someone point that code to me or am I mistaken ?
 
For a feeder to a disconnect switch I cannot give you code reference because there isn't one. There are conditions however where a service will require a grounded conductor to be brought to it.
 
Outlawkyote said:
I coulda swore that I saw a code stating that all disconnects are required to have a neutral pulled to them weather the neutral is used or not.

I cant find that code anymore and the question has rissen in our shop. Can someone point that code to me or am I mistaken ?

Are you thinking about 300.20 perhaps?
 
Trevor is correct, it is only for Service Equipment, see 250.24(C)

Roger
 
roger said:
Trevor is correct, it is only for Service Equipment, see 250.24(C)

Roger

Thanks Roger
Thats the code I remember seeing but couldnt remember what the exact circumstances were.

Thanks to everyone who replied
 