Neutral Conductor Article NEC 310.15

Status
Not open for further replies.

zabawire

Member
The following question is in regard to NEC 2008 article 310.15 (B) (4). It is not apparent to me if the neutral conductor for the following voltage systems:

120/240 volt( 3 wire, single phase), 120/208 volt(4w, grounded Wye, three phase), 277/480 volt (4w,grounded Wye,three phase)

is considered a current-carrying conductor or not for the purpose of applying Table 310.15(B)(2)(a). Please advise as appropiate
 
For the 120/240 volt single phase, the neutral is never required to be counted as a current carrying conductor when it is part of a 3 wire circuit. For the other two, when part of a 4 wire circuit, with the majority of the loads linear, the neutral is not counted as a current carrying conductor. If a majority of the load is non-linear, then it is counted. Also when using two ungrounded conductors and a grounded conductor from a 3 phase wye system the neutral is always a current carrying conductor.
 