Neutral conductor lands on neutral bar opposite from circuit breaker.

Status
Not open for further replies.

djharkins47

Member
Location
Port Angeles, WA
Occupation
DIY
Why is the neutral conductor for a bathroom circuit with a GFIC outlet landed on the neutral bar on the opposite side of the breaker panel from the bathroom circuit breaker?
 
Electrically it doesn't matter as long as it's on a neutral bar. It just might be that physically the installer put it there because it was easier or maybe more direct or maybe the only place available if the circuit was added later. There is nothing that says the neutral and breaker have to be near each other.

-Hal
 