NEC Forum Gurus,
I want to place 13 conductors in one conduit (6 single-phase, 120V circuits; 6-hots, 6-neutrals (no shared neutrals) and (1)-ground). Concerning the neutral, I interpret 310.15(5)(a) to apply where I do not have to count the neutral conductor as a current carrying conductor when applying Table 310.15(B)(3)(a). Does anyone see an issue with this?
Thanks for any and all responses.
Steve
I want to place 13 conductors in one conduit (6 single-phase, 120V circuits; 6-hots, 6-neutrals (no shared neutrals) and (1)-ground). Concerning the neutral, I interpret 310.15(5)(a) to apply where I do not have to count the neutral conductor as a current carrying conductor when applying Table 310.15(B)(3)(a). Does anyone see an issue with this?