Neutral Conductor

Status
Not open for further replies.

Cards

Member
I am replacing a meter bank on a multi family dwelling. This is a single phase 120/240 V system. The feeders are rated for 125 A. I am going to set a trough and pipe over to one side of the MB. I will run 3 sets of feeders in the conduit. The inspector says I must count each neutral as a current carrying conductor. Unless I am not reading this correctly 310-15 (B) (5) says only 3-wire circuit of a 4-wire,3-phase wye connected system be counted. So instead of 6 current carriers I now have 9. That will make a big difference on my end. I would appreciate some feedback
 
Basically a 3 wire feeder neutral conductor nstalled in a single phase panel would NOT be counted as a current carrying conductor.
 
Basically a 3 wire feeder neutral conductor nstalled in a single phase panel would NOT be counted as a current carrying conductor.
...including 3 sets of 120/240 1Ø 3W feeders. The inspector may be thinking it is a 120/208 setup from 208/120 source.
 
I am replacing a meter bank on a multi family dwelling. This is a single phase 120/240 V system. The feeders are rated for 125 A. I am going to set a trough and pipe over to one side of the MB. I will run 3 sets of feeders in the conduit. The inspector says I must count each neutral as a current carrying conductor. Unless I am not reading this correctly 310-15 (B) (5) says only 3-wire circuit of a 4-wire,3-phase wye connected system be counted. So instead of 6 current carriers I now have 9. That will make a big difference on my end. I would appreciate some feedback

You are correct, the inspector is wrong on this one.
 
Make sure inspector realizes you have 180 degree vs 120 degree phase differential and understands the requirement associated with each.
 