Can someone please explain 310.15 A 4? Are the talking about an Edison circuit out of a 120/240 volt single phase service? If i have a 4 wire circuit 120/208 or 277/480 consisting of 3 phase conductors with a neutral is the neutral counted?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Can someone please explain 310.15 A 4? Are the talking about an Edison circuit out of a 120/240 volt single phase service?
No, in a 120/240 volt system the neutral would never need to be counted in an Edison circuit.
If i have a 4 wire circuit 120/208 or 277/480 consisting of 3 phase conductors with a neutral is the neutral counted?
Only if the majority of the load served is non-linear.

If you are using a three wire Edison circuit from a 120/208 volt Wye system the neutral would be counted.

Roger
 