I recently saw the following question based on the 2008 NEC
What size feeder conductors are required for a 200A continuous load if the terminals are rated 75C?
A. 2/0 AWG ungrounded and 1/0 AWG neutral conductors
B. 3/0 AWG ungrounded and 1/0 AWG neutral conductors
C. 4/0 AWG ungrounded and 1/0 AWG neutral conductors
D. 250 kcmil ungrounded and 3/0 AWG neutral conductors
The answer given was "D"
I think all of the above answers are wrong. The neutral, IMO, should be 4/0 AWG given the required size of the OCPD is 250A.
Comments welcome.