electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
I am pricing out a job where I need to feed 104 1000 watt HPS electronic ballasts. I need to design both the branch circuits and the feeder. The system is 277/480 and the lights will be on MWBC's. So you know where this is going In regards to the neutral being a CCC, and for sizing the neutral conductor, It seems like there is no other way than to get a hold of three of the lights and clamp the neutral and scope the line conductors? The system will be balanced so I would like to use the smallest neutral possible, sized to 250.122, but I cant be sure of the harmonic currents. Does a "total harmonic distortion" from the spec sheet give anything meaningful? I am sure this comes up all the time when lighting systems for office buildings are designed/installed, what is typically done?