Hello everyone, first time posting here.
I have a question regarding parallel feeders. In a design presented by a client, the ungrounded conductors are divided into three parallel conductor sets, but the neutral is only installed in two sets, sized for a lower ampacity. There is also a single equipment grounding conductor.
Before I proceed, I want to confirm whether this complies with the NEC.
The entire run between equipment is installed in cable tray, including the vertical drop to the equipment. I understand that only one equipment grounding conductor is required for the feeder in the tray, but I am not sure about the neutral.
Is it permissible to install only two (2) neutral conductors in parallel, or must the neutral also be run in three (3) conductors just like the ungrounded conductors?
Any guidance or code references would be appreciated.
I have a question regarding parallel feeders. In a design presented by a client, the ungrounded conductors are divided into three parallel conductor sets, but the neutral is only installed in two sets, sized for a lower ampacity. There is also a single equipment grounding conductor.
Before I proceed, I want to confirm whether this complies with the NEC.
The entire run between equipment is installed in cable tray, including the vertical drop to the equipment. I understand that only one equipment grounding conductor is required for the feeder in the tray, but I am not sure about the neutral.
Is it permissible to install only two (2) neutral conductors in parallel, or must the neutral also be run in three (3) conductors just like the ungrounded conductors?
Any guidance or code references would be appreciated.