What would happen hypothetically if a 480-208/120 transformer fed a 208V three phase panelboard but there were only 3W+G ran between the transformer secondary and the panel and therefore there is no neutral pulled to panel. The transformer secondary wye point is solidly grounded at the transformer.
Now lets say out of the panel there is a branch circuit which feeds a single phase 120V load. The hot wire is ran through the branch breaker to the load as normal however the neutal wire from the load is ran straight back to the neutral or wye point of the transformer since there was no neutral pulled to the panel.
Other than the obvious code violations is there anything strange that would occur within panel feeder circuit or branch circuit from this arrangement (ignoring any ground fault detection that may be present). From what I can tell the load will operate fine as will the rest of the circuit and the only issues are related to code violations?
Now lets say out of the panel there is a branch circuit which feeds a single phase 120V load. The hot wire is ran through the branch breaker to the load as normal however the neutal wire from the load is ran straight back to the neutral or wye point of the transformer since there was no neutral pulled to the panel.
Other than the obvious code violations is there anything strange that would occur within panel feeder circuit or branch circuit from this arrangement (ignoring any ground fault detection that may be present). From what I can tell the load will operate fine as will the rest of the circuit and the only issues are related to code violations?