Hello all I have used this forum for some time and have found the advice very useful, however this is my first post on this forum.
My request concerns a 4 wire low voltage network (230v phase to neutral) connected to a delta wye transformer.
I understand that when the load across the 3 phases is not equal current flows in the neutral conductor and the greater the unbalance the greater the current flowing.
What I would like explained is in regard to losses. If the neutral current was say 10amps does this mean the feeder cable is drawing an additional 10amps (measured at the substation)? So the losses over the day would be 10x24 = 240 Ah @ 250V = approx 60kWh.
Or is the losses simply calculated from IxIxR?
If so can someone explain the current flowing in the neutral conductor please.
Thanks in advance
Sent from my iPhone using Tapatalk