I was reading an article on transformers at www.federalpacific.com/university/kfactor/chapter3.html It states the following..."In a 3-phase, 4-wire system, single-phase line-to-neutral currents flow in each phase conductor and return in the common neutral. Since the three 60 hertz currents are separated by 120?, when balanced they cancel each other. The measured resultant current is equal to zero." I don't understand, if the current is zero, how does anything work?? Lights don't come on with 0 current flow. What are they trying to say? If I remember correctly it is legal to share a neutral in a 120V branch circuit if the loads are fed from 3 different phases. Is this the reasoning? (I have always ran a neutral for every circuit anyway, but I have heard of people sharing)
Also,
In chapter 2 of the same website, they state that the neutral connection of a transformer should be rated at 200% of the phase ratings of the phase connections, to account for harmonics. Is it a good idea to oversize individual branch circuit neutrals at 200% or just the neutral between the panel board and the transformer? It seems that the theory would follow.
Thanks. I like this website, everyone is very helpful.
Shawn
Also,
In chapter 2 of the same website, they state that the neutral connection of a transformer should be rated at 200% of the phase ratings of the phase connections, to account for harmonics. Is it a good idea to oversize individual branch circuit neutrals at 200% or just the neutral between the panel board and the transformer? It seems that the theory would follow.
Thanks. I like this website, everyone is very helpful.