JerryBumgarner
Member
We are connecting a Trojan UV system. It calls for a 3 phase, 208Y, 4 wire connection. We are providing that power to the system. When the Trojan field rep was starting up the system today, she measured the current in each phase with all 3 UV modules connected. The current was 12 amps in each phase (that was rated current). She then measured the neutral current - 10.8 amps. She will not sign off on the start up unless the neutral current is < 5 amps. I agree that the neutral current should be small. However, I am arguing that the load (UV system) is causing the neutral current. She is arguing that we are providing an unbalanced system to them and that the problem is on our end. Has anyone seen anything similar to this?
Background: This is a new waste water treatment plant and we are the EC. The plant is not running yet so the only load on the transformer is the UV system and the 4 lights that were on in the electric room. Incoming power is 3 phase 480. It is being stepped down to 208 using a 480 Delta/208Y transformer. The transformer supplies a distribution panel and the UV system is fed from a 3 pole, 20 amp breaker. The lamps of the UV system are all connected line-to-neutral (3 lamp modules per system). There are 2 UV systems and both have the same phase and neutral currents. The line-to-line voltage measures 215 VAC (Duke Energy is always high here). Line-to-neutral voltage measures 125 VAC. The neutral of the transformer secondary is bonded to ground. The transformer is grounded to 3 ground rods driven in a triangle.
Background: This is a new waste water treatment plant and we are the EC. The plant is not running yet so the only load on the transformer is the UV system and the 4 lights that were on in the electric room. Incoming power is 3 phase 480. It is being stepped down to 208 using a 480 Delta/208Y transformer. The transformer supplies a distribution panel and the UV system is fed from a 3 pole, 20 amp breaker. The lamps of the UV system are all connected line-to-neutral (3 lamp modules per system). There are 2 UV systems and both have the same phase and neutral currents. The line-to-line voltage measures 215 VAC (Duke Energy is always high here). Line-to-neutral voltage measures 125 VAC. The neutral of the transformer secondary is bonded to ground. The transformer is grounded to 3 ground rods driven in a triangle.