I just got done taking (2) weeks worth of power readings on the secondary of a 2000kVA 480V/277V wye secondary transformer. The neutral point of the transformer is solidly grounded. We do not use a neutral from the transformer and therefore only have 3-wires + gnd feeding two MCC's off off two seperat breakers.
I went back and looked at trends and saw that the average neutral current reading was about 5A. This current was measured directly with a CT on the neutral bus.
Why am I seeing neutral current if I have no L-N loads connected on the secondary of the transformer? Is this a result of capacitive coupling to ground?