Neutral Currents in a Wye:g Transformer

Status
Not open for further replies.

ChrisCentral

Member
Location
Ontario
I have an incoming service to a building at 347/600V Wye:g, 600A. A contractor has installed a step down transformer 347/600V to 480V Delta, the inspector passed the installation but now the transformer is overheating and there are both Neutral and Ground currents. I read through 'The Wyes of Wyes' but I can't get a clear answer on the issue - to make matters worse the transformer mfg doesn't 'necessarily see a problem with the connection as it has been completed'.... please help :?
 
I think your idea is to break the path for stray current through the transformer. But disconnecting primary neutral ground connection will give rise to unsymmetrical secondary voltages for unbalanced loads on a wye wye transformer.
 
But disconnecting primary neutral ground connection will give rise to unsymmetrical secondary voltages for unbalanced loads on a wye wye transformer.
Then it is a good thing that is not a concern for the OP since that is not what the OP has.
 