Article 220.61 (C) (2) States that there shall be no reduction of the neutral or grounded conductor capacity for that portion consisting of nonlinear loads supplied from a 4-wire, wye-connected, 3-phase system.
My question is regarding load calculating the size of a neutral conductor when there are nonlinear loads involved.
Article 220.61 (B) (2) states that the portion of the unbalanced load in excess of 200 amps where the feeder or service or feeder is supplied from a 3-wire dc or single-phase ac system, or a 4-wire, 3-phase: 3-wire, 2 phase system, or a 5-wire, 2-phase system shall be permitted to have an additional demand factor applied.
Does the whole calculated neutral amount above the 200amps fall into the permitted reduction of 220.61 (B)? Or do I need to take out the calculated nonlinear neutral load and not de-rate that portion, then take the first 200amps of the linear load at 100% and any additional linear load above 200amps at 70%? Then add those figures to get my calculated neutral load?
My question is regarding load calculating the size of a neutral conductor when there are nonlinear loads involved.
Article 220.61 (B) (2) states that the portion of the unbalanced load in excess of 200 amps where the feeder or service or feeder is supplied from a 3-wire dc or single-phase ac system, or a 4-wire, 3-phase: 3-wire, 2 phase system, or a 5-wire, 2-phase system shall be permitted to have an additional demand factor applied.
Does the whole calculated neutral amount above the 200amps fall into the permitted reduction of 220.61 (B)? Or do I need to take out the calculated nonlinear neutral load and not de-rate that portion, then take the first 200amps of the linear load at 100% and any additional linear load above 200amps at 70%? Then add those figures to get my calculated neutral load?