Hello,
I had an electrical inspection yesterday and failed because I did not consider the “conductor derating” code. We ran #12 wires 6 hot and 6 neutral in a 3/4” Emt conduit from the electrical panel to the pull box, the length is 28”. The inspector’s argument is that we have more than three current carriers, which derates the conductors. From my understanding is that the inspector’s concern was the excessive heat that will be created when having more than three current carriers. ALTHOUGH, my electrician’s counter argument is that there won’t be any heat, because each hot wire is balanced with one neutral; 6 hot and 6 neutral. Does that make any sense or not?
I had an electrical inspection yesterday and failed because I did not consider the “conductor derating” code. We ran #12 wires 6 hot and 6 neutral in a 3/4” Emt conduit from the electrical panel to the pull box, the length is 28”. The inspector’s argument is that we have more than three current carriers, which derates the conductors. From my understanding is that the inspector’s concern was the excessive heat that will be created when having more than three current carriers. ALTHOUGH, my electrician’s counter argument is that there won’t be any heat, because each hot wire is balanced with one neutral; 6 hot and 6 neutral. Does that make any sense or not?