If you are using a neutral with 2 ungrounded conductors of a 3 phase wye system, it is always a current carrying conductor. If you are using it with all 3 ungrounded conductors it is a current carrying conductor only if the majority of the load is non-linear.I have a 120/208 3 phase panel feeding lighting and receptacle circuits sharing 1 neutral for two to three circuits. Do I need to count the neutral as a current carrying conducter?
Well i maybe incorrect please correct me , but 3 phase its the unbalanced load on that neutral of the 3 legs meaning it has to be counted and that is feeder or branch circuit if A B C is connected to a neutral then it has current flow thur it which effects temp in conduit . comments ? best to ya