I need to size my neutral conductor that will be connected to the H0 terminal of my neutral deriving transformer.
I have never size one before, so I seek advice or recommendations.
Below is the specification of the NDT:
System Voltage: 480V Wye 3-Phase
Transformer Voltage: 480ZZ/277V
Continuous kVA: 57.00
X0 = 0.1759 ohm (plus-minus 10%)
3Io Current Approximately = 4,700A
X0/R0 > 4
Neutral Current: 189A - Continuous, 63A per leg
3963A - 4S
In my understanding, I need to size my neutral conductor to not exceed the total allowed neutral current of the NDT which is 189 amps.
Will a #2/0 AWG copper suffice? Do I need to consider any other things aside from the neutral current rating that my NDT can handle during normal operating conditions?
Thank you and I highly appreciate all the response and assistance.