I have 2 questions, somewhat related:
1) When you have multiple service switches, including the switches for any fire pumps and the fire alarm system, does every switch (including the fire alarm disconnect switch) require the neutral disconnect link that's required in the NEC?
2) Does the main bonding jumper connection inside each service switch, and the connection to the grounding electrode conductor, happen on the load side of the neutral disconnect link? I would imagine yes, because if you disconnect the neutral link for any servicing, you still want to maintain the GEC connection and the MBJ connection.
Thanks!
I have 2 questions, somewhat related:
1) When you have multiple service switches, including the switches for any fire pumps and the fire alarm system, does every switch (including the fire alarm disconnect switch) require the neutral disconnect link that's required in the NEC?
2) Does the main bonding jumper connection inside each service switch, and the connection to the grounding electrode conductor, happen on the load side of the neutral disconnect link? I would imagine yes, because if you disconnect the neutral link for any servicing, you still want to maintain the GEC connection and the MBJ connection.