Hello All
Bonding of Earth and neutral in machine subpanels will cause a problem, but I want to know how it would affect PLC & VFD, etc.
The machine has 2 panels one for heaters (uneven load in each phase) another has VFD (250 kW) for the motor. since the last 4 months continuously facing a problem with drive most of the time control board failed without any error replaced with new VFD but no improvement. Also found some liquid from boards maybe electrolyte.
While checking found both panel earth & neutral & bonded together. I removed the bonding but want know to make sure it was the root cause of all the time drive failure.
Also After removing bonding in the sub-panel between earth & neutral showing some 100kohms. The main panel (transformer room) & subpanel earth are not connected then how showing some ohms and it keeps varying. In a cable have 4 wire i.e 3 phase & 1 neutral.
Please advice..
Bonding of Earth and neutral in machine subpanels will cause a problem, but I want to know how it would affect PLC & VFD, etc.
The machine has 2 panels one for heaters (uneven load in each phase) another has VFD (250 kW) for the motor. since the last 4 months continuously facing a problem with drive most of the time control board failed without any error replaced with new VFD but no improvement. Also found some liquid from boards maybe electrolyte.
While checking found both panel earth & neutral & bonded together. I removed the bonding but want know to make sure it was the root cause of all the time drive failure.
Also After removing bonding in the sub-panel between earth & neutral showing some 100kohms. The main panel (transformer room) & subpanel earth are not connected then how showing some ohms and it keeps varying. In a cable have 4 wire i.e 3 phase & 1 neutral.
Please advice..