Neutral for 120 volt circuit
tom baker
Bremerton, Washington
Master Electrician
Here are the definitions of neutral and neutral point
Neutral Conductor. The conductor connected to the neutral point of a system that is intended to carry current under normal conditions.
Neutral Point. The common point on a wye-connection in a polyphase system or midpoint on a single-phase, 3-wire system, or midpoint of a single-phase portion of a 3-phase delta system, or a midpoint of a 3-wire, direct-current system.
Does a 120 secondary of a transformer have a neutral or a grounded conductor?
The definition of grounded conductor has been deleted.
But Article 200 still uses the term grounded conductor.
Maybe I think too much.
Both ------space filler
If it did not, i know of one transformer that would be getting returned to the supplier:grin:
x2 per Jim
If the definition has changed and a single winding xformer therefore might not fall under all of the restrictions of a neutral conductor??
If it is a single winding secondary with one end grounded, I believe you can call it either when other grounded systems having a grounded neutral point are also on premises.
If neither end is grounded (which may or may not be compliant), you can't call any attached conductor a Neutral conductor or a grounded conductor.
tom baker said:
. . . Does a 120 secondary of a transformer have a neutral or a grounded conductor? . .
From the 2008 Edition of the NEC, "Grounded Conductor. A system or circuit conductor that is intentionally grounded."
If a transformer has a single 120 volt winding, it does not have a neutral but it does have a grounded conductor. If a transformer has two 120 volt windings that may be connected in series and center point grounded, it does have a neutral and it does have a grounded conductor (same one). If you are running a 120 volt circuit from a 120/240 volt 1? panelboard, the circuit has a neutral and an ungrounded conductor.
A corner grounded delta does not have a neutral but it has a grounded conductor.