Neutral for a 120/208y 300 amp service

Status
Not open for further replies.

delectric123

Senior Member
Location
South Dakota
I am installing a 120/208y 300 amp breaker panel. the service conductors are 300 MCM Cu with an current rating of 285 amps without derating. As, of right now, the loads are 3 - 20 HP 3 ph. pumps, and a few lights and a few outlets. i'm sure i definitely don't need to count the neutral as a CCC, but can i downsize it? By how much? Whats the code reference to it?
 

david

Senior Member
Location
Pennsylvania
230.42 Minimum Size and Rating.

220.61 Feeder or Service Neutral Load.
(A) Basic Calculation.

(B) Permitted Reductions. A service or feeder supplying the following loads shall be permitted to have an additional demand factor of 70 percent applied to the amount in 220.61(B)(1) or portion of the amount in 220.61(B)(2) determined by the basic calculation:
 
Last edited:

kwired

Electron manager
Location
NE Nebraska
In general it only needs sized to the maximum calculated imbalanced current it will carry.

In no case can it be smaller than the GEC as mentioned in 250.24(C) for services.

For feeders or branch circuits it can not be smaller than the required EGC see 215.2(A)(2) for feeders.
 