I need to move a 50 amp single phase 208 volt Seimans GFCI breaker (which is installed in a lighting panel) feeding a transfer switch. The transfer switch feeds a portable steam cleaner and a "bearing heater" because it was determined that the mechanics would rarely, if ever, need to use both at once in this shop. The "bearing heater" is an old 3 wire GE kitchen range. The range will trip the GFCI breaker intermittently. I have been through it and the main oven element meggers 50k to ground. There are other low readings on the broil and cleaning elements, but this is the lowest and the only one used for heating bearings.The breaker doesn't seem to like this. The guick fix would be to put the required (at least for the steam cleaner) GFCI breaker down stream of the transfer switch. I would like to tap a short run of neutral from nearby to save running a "dedicated" neut. for the breaker some 200 ' back to the panel. Knowing GFCI outlets don't work on shared neutrals, I'm wondering if the breaker will be the same. I never understood why sharing a neut on GFCIs was a problem as they are all "common" back to the neutral bar anyway. Any ideas?
Thanks.
Thanks.