- Tennessee NEC:2017
- Occupation
- Semi-Retired Electrician
By portable I don't mean the small resi type generators. I'm talking about one such as a 75 KW 3 phase that you would rent to use on a job site.
With that said, does the neutral/grounded conductor need to be brought out to equipment or a power distribution box if all the equipment is line-line?
I'm trying to figure out what would cause the OCPD to operate should a line to ground fault occur somewhere downstream of the generator.
Is the grounded conductor and EGC bonded on the generator so that the EGC would be the fault path back to the generator?
With that said, does the neutral/grounded conductor need to be brought out to equipment or a power distribution box if all the equipment is line-line?
I'm trying to figure out what would cause the OCPD to operate should a line to ground fault occur somewhere downstream of the generator.
Is the grounded conductor and EGC bonded on the generator so that the EGC would be the fault path back to the generator?