I have a shelter that has an onboard generator as well as a shore input. The generator is hard wired to an off the shelf panel that is normally used for home installation. The generator and shore input are back fed through their own breaker. There is a switch on these breakers to prevent them both from being closed at the same time. The panel is a 240V single phase panel and the backfed breakers are 2 pole breakers.
There is also a neutral ground bond at the generator which is fine when running on generator power. When the shelter is on shore power, however, it is assumed that the shore source has a neutral ground bond somewhere up stream. I believe this is a problem? Any ideas on how I break the neutral ground bond at the generator when running on shore power easily so that an unskilled operator of the shelter can make the switch?
Another question is since the input power is 208V or 240V single phase and all loads are 208V or 240V single phase is the neutral conductor even necessary?
There is also a neutral ground bond at the generator which is fine when running on generator power. When the shelter is on shore power, however, it is assumed that the shore source has a neutral ground bond somewhere up stream. I believe this is a problem? Any ideas on how I break the neutral ground bond at the generator when running on shore power easily so that an unskilled operator of the shelter can make the switch?
Another question is since the input power is 208V or 240V single phase and all loads are 208V or 240V single phase is the neutral conductor even necessary?