Neutral ground bonding- After Transformer

Status
Not open for further replies.

mathan1987

Member
Location
Seattle
Occupation
Electrical design engineer
Hi

I am connecting a 208V panel at secondary side of a 480V/ 208V Y transformer. Is it enough to bond the neutral and ground at transformer or Do i need to bond the Neutral and ground in the 208V panel as well.

thanks
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
Hi

I am connecting a 208V panel at secondary side of a 480V/ 208V Y transformer. Is it enough to bond the neutral and ground at transformer or Do i need to bond the Neutral and ground in the 208V panel as well.

thanks
Only bond in one or the other, or else you will create a path for parallel neutral current.
 