wesley1
Member
- Location
- Port St. Joe, Florida
- Occupation
- Electrical contractor owner
new modular office building my company supplying underground sevice to is a double wide. 1 side has a 150 amp single phase 240 volt non fused disconnect and the other side has a 200 amp single phase 240 volt non fused disconnect. Directly thru wall on inside of each is a 150 amp panel and a 200 amp panel respectively. We are planning on installing 400 amp meter base in the center and feed off load side with double lugs to each disconnect. The wire length to disconnects are only 7' so tap rule should allow for less than 10 feet. As i try to design this though i have a question about where the neutral and grounds should be bonded togethor. The answer may simply be i will have to install a single 400 amp disconnect. I was trying to eliminate cost of this but might be unavoidable. The panels inside have a bonding strap that has each panels neutrals buss bonded. but im a wrong in saying that with 2 seperate panels they should not be bonded as you only want gec and egs bonded at 1 place? Also the supplied disconnects in picture does not have neutral lugs. Thus in the manufacturers design i dont think intended to be bonded there. Reading article 250 and 550 still. Any input would be appreciated.