sparky_pdx
Member
Hi,
1st time poster. I'm a journeyman electrician in Portland. Mostly do residential, but have a commercial question. New 200A service, meterbase
& mast @ front of building, 60' pipe outside wall, LB directly to panel inside.
Power company wants a metermain instead of meterbase. Already have 3 wire service conductor, 4/0, 4/0, 2/0 Al. Per tables in 250, I'm pretty sure I can just add a #4 Cu Ground into pipe & seperate Neutral & Ground bus in Panel. Just wanna be sure. I noticed that 4w, 200A SER cable has 4/0, 4/0, 4/0, 2/0 Al. 1 other quick question, bonding of gas & water pipe can happen anywhere, not just 5' from entrance.
Thanks in advance.
Sparky
1st time poster. I'm a journeyman electrician in Portland. Mostly do residential, but have a commercial question. New 200A service, meterbase
& mast @ front of building, 60' pipe outside wall, LB directly to panel inside.
Power company wants a metermain instead of meterbase. Already have 3 wire service conductor, 4/0, 4/0, 2/0 Al. Per tables in 250, I'm pretty sure I can just add a #4 Cu Ground into pipe & seperate Neutral & Ground bus in Panel. Just wanna be sure. I noticed that 4w, 200A SER cable has 4/0, 4/0, 4/0, 2/0 Al. 1 other quick question, bonding of gas & water pipe can happen anywhere, not just 5' from entrance.