I have a solidly grounded, 480/277-volt 1200 ampere service with ground
fault protection on the incoming main. I wish to add a 480/277 volt,
stand-by generator that will be connected as a alternate source of power to
selected loads via an 800-ampere automatic transfer switch. The generator
is intended to operate only during utility power outages. It is not a
legally required emergency supply. My question is whether or not the NEC
specifically requires that there be a 4-pole, switched neutral ATS and
separate grounding of the generator neutral for this installation. It is
realized that if the generator neutral were not separately grounded, and
that a ground fault were to occur while the generator were running, the main
disconnect would trip and would not isolate a low level fault. But because
the generator would only be in operation if the utility supply were out, I
don't understand if that, per se, although an irritation, is, or is not a
violation of code.
fault protection on the incoming main. I wish to add a 480/277 volt,
stand-by generator that will be connected as a alternate source of power to
selected loads via an 800-ampere automatic transfer switch. The generator
is intended to operate only during utility power outages. It is not a
legally required emergency supply. My question is whether or not the NEC
specifically requires that there be a 4-pole, switched neutral ATS and
separate grounding of the generator neutral for this installation. It is
realized that if the generator neutral were not separately grounded, and
that a ground fault were to occur while the generator were running, the main
disconnect would trip and would not isolate a low level fault. But because
the generator would only be in operation if the utility supply were out, I
don't understand if that, per se, although an irritation, is, or is not a
violation of code.