Neutral Grounding Resistor Cable

Status
Not open for further replies.

big john

Senior Member
Location
Portland, ME
The conductor between the NGR and the neutral point of your transformer absolutely needs to be rated at full system voltage, because during a hard ground-fault it will assume L-G potential.

The conductor bonding the NGR to your grounding pad will see a lot of current flow, but shouldn't see a significant voltage rise. My opinion is that this does not to be insulated. That said, I have seen that installed as both insulated and uninsulated.

As far as stress cones, yes, I think 310.10(E) makes it pretty plain that most MV cable must be shielded. This would be especially true if you're running anything other than a 100% insulation level where you could have a sustained fault and prolonged stress on the cable.
 