sindhu04
New member
- mumbai,india
How to size neutral grounding resistors for both low voltage and high voltage systems per IEEE standard or NEC code.
Sindhu04...
The premise behind resistance-grounding of a system-neutral at any voltage level, is to mitigate the effects of ground-fault current, i.e., burned-insulation, and/or melted magnetic-iron.
A LV system-neutral can certainly be grounded through an impedance to limit fault-current magnitude (of the order of tens of thousands of kVA) but solid-grounding eliminates the need to install more sensitive ground-fault detectors on every feeder circuit-breaker. The phase-over-current protective device is usually sufficient. Repair or replacement of LV equipment is relatively easier to handle, both in material and cost!
Of course, any MV system-neutral can be solidly-grounded, but the resultant ground-fault current is much greater than LV systems (of the order of hundreds of thousands of kVA.) Also, if damage is kept low, repair is possible. If, however, current magnitude is very large, the magnetic-structure damage may preclude repair, but instead will require total replacement. Thus, resistance-grounding of a MV system-neutral is more of an economic choice. Almost with certainty, the Benefit-to-Cost Ratio justifies its implementation.
Regards, Phil Corso