neutral grouping

Status
Not open for further replies.
I'm on a job with a new company. I'm told a branch circuit neutral within a panelboard must be grouped with its phase conductor in at least one location per 2008 NEC code requirements, multiwire branch circuit or not.

I know of only 210.4, pertaining to mwbc. ?
 
It's only required when there is more than a MWBC in a raceway or cable. A raceway with one, two or three circuits sharing a neutral would not be required to be grouped.
 