For service equipment the grounded conductor must be either opened by the service disconnecting means or be able to be disconnected from the supply by other means - typically by being able to remove it from a lug or bus. (see 230.75 for this requirement)
For feeders, there is no requirement to be able to disconnect the grounded conductor from the supply that I am aware of and another question that comes up is how can you be required to land a conductor that isn't necessarily required to be there in the first place? Based on that I'd say pulling it through unspliced should be acceptable.