Ed,
There is only the meter in front of the TS and the TS is rated as service equipment. I was just looking at the diagram on the door of the TS and it shows when it is used as service equipment that the neutral needs to be bonded to the can.Should I run the #6 ground from the meter unbroken into the TS and bond it with a grnd lug and then bond the N to the can. Also the customer has not bought the generator yet so I don't know if the N is switched in it or not.Thanks for the diagrams they help a great deal.Didn't mean to repost :roll:
There is only the meter in front of the TS and the TS is rated as service equipment. I was just looking at the diagram on the door of the TS and it shows when it is used as service equipment that the neutral needs to be bonded to the can.Should I run the #6 ground from the meter unbroken into the TS and bond it with a grnd lug and then bond the N to the can. Also the customer has not bought the generator yet so I don't know if the N is switched in it or not.Thanks for the diagrams they help a great deal.Didn't mean to repost :roll: