5 5xr4uu7 New member Location dollar Jul 4, 2017 #1 Where in the code does it say that you cannot bond a neutral and the ground at the subpanel? having trouble finding it. thanks
Where in the code does it say that you cannot bond a neutral and the ground at the subpanel? having trouble finding it. thanks
Smart $ Esteemed Member Location Ohio Jul 4, 2017 #2 250.24(A)(5) for grounded service-supplied systems and 250.30(A) for grounded separately derived systems.
250.24(A)(5) for grounded service-supplied systems and 250.30(A) for grounded separately derived systems.
kwired Electron manager Location NE Nebraska Occupation EC Jul 4, 2017 #3 You used to be able to do so for separate buildings, with some conditions. Now there is only exception for existing ijnstallations that allowed it when it was installed-still with conditions.
You used to be able to do so for separate buildings, with some conditions. Now there is only exception for existing ijnstallations that allowed it when it was installed-still with conditions.