Where in the code does it say that you cannot bond a neutral and the ground at the subpanel?
having trouble finding it.

thanks
 
250.24(A)(5) for grounded service-supplied systems and 250.30(A) for grounded separately derived systems.
 
You used to be able to do so for separate buildings, with some conditions.

Now there is only exception for existing ijnstallations that allowed it when it was installed-still with conditions.
 