jim k
Member
- Location
- Northwestern Oregon
In my area, there are hundreds ? perhaps even thousands ? of subpanels that are supplied by three-wire feeders and that have their equipment grounding conductors terminated in the neutral terminal bars. It?s only in installations that were done in the last 10 years or so that I see 4-wire feeds and isolated neutrals.
When I?ve asked about this, the ECs always say, ?Ground-neutral separation at sub-panels didn?t used to be required. It?s a new thing.? But they can never give me chapter & verse.
As I read 250.24(A)(5) in the 2005 NEC it seems pretty clear on the point. But so does 250-61 in the 1993 edition. In fact, that section seems to have changed very little since the 1947 edition (the oldest one I own):
The grounded circuit conductor on the load side of the service disconnecting means shall not be used for grounding equipment, cable armor, or metal raceways except as provided in paragraph c of section 2557; and in section 2560.
I know that article 250 was drastically reorganized in 1999, but the substance of this particular requirement doesn?t seem to have changed.
Is it common in other parts of the country to find older subpanels with no ground ? neutral separation?
If so, why? Hasn?t it always been prohibited? Is there a NEC section or exception that I?m missing regarding this?
- Jim Katen, Oregon
When I?ve asked about this, the ECs always say, ?Ground-neutral separation at sub-panels didn?t used to be required. It?s a new thing.? But they can never give me chapter & verse.
As I read 250.24(A)(5) in the 2005 NEC it seems pretty clear on the point. But so does 250-61 in the 1993 edition. In fact, that section seems to have changed very little since the 1947 edition (the oldest one I own):
The grounded circuit conductor on the load side of the service disconnecting means shall not be used for grounding equipment, cable armor, or metal raceways except as provided in paragraph c of section 2557; and in section 2560.
I know that article 250 was drastically reorganized in 1999, but the substance of this particular requirement doesn?t seem to have changed.
Is it common in other parts of the country to find older subpanels with no ground ? neutral separation?
If so, why? Hasn?t it always been prohibited? Is there a NEC section or exception that I?m missing regarding this?
- Jim Katen, Oregon