donf
Member
- Location
- Tidewater Virginia
In the 2008 edition of code, citation 210.19(A)(1) Exception #2 was introduced.
This exception allowed you to size the Neutral conductor at 100% of the continuous load plus 100% of the non continuous load.
The 2011 edition as well as the pending 2014 edition do not have this exception.
Question, was this exception incorporated somewhere else or do we now size the Neutral load at 125% of the continuous load plus 100% of the non continuous load?
This exception allowed you to size the Neutral conductor at 100% of the continuous load plus 100% of the non continuous load.
The 2011 edition as well as the pending 2014 edition do not have this exception.
Question, was this exception incorporated somewhere else or do we now size the Neutral load at 125% of the continuous load plus 100% of the non continuous load?
Last edited: