Attached is pic of panel schedule and unit schedule for these two units. It's a 3P4W panel, not sure why that would matter.
It's a pump that's being feed. So according to the schedule it's just one phase conductor but I would certainly pull a separate ground for a unit like this. My question is how does one determine if a neutral would be needed? I know a lot of motors don't need a neutral.
 

Attachments

  • Capture 1.JPG
    Capture 1.JPG
    45.2 KB · Views: 15
  • Capture.JPG
    Capture.JPG
    201.7 KB · Views: 15
My question is how does one determine if a neutral would be needed? I know a lot of motors don't need a neutral.
No motor requires a neutral (grounded conductor) per se, but does require two conductors (3 for 3ph).

A motor rated at 115v will receive one because our 120v supplies almost always happen to include one.
 
No motor requires a neutral (grounded conductor) per se, but does require two conductors (3 for 3ph).

A motor rated at 115v will receive one because our 120v supplies almost always happen to include one.
You say a motor requires 2 conductors( that would be 208v. But if it's a case like this 120v it would only require one conductor, a hot??
 
On a 208/120V system.

A motor rated 115v will receive one _neutral_. Two conductors, a hot and a neutral. The 115V rating implies single phase, and the system implies a hot and a neutral.

A single phase 208V motor will receive two hots, but no neutral.

A three phase 208V motor will receive three hots, but no neutral.

-Jon
 
You say a motor requires 2 conductors( that would be 208v. But if it's a case like this 120v it would only require one conductor, a hot??
I don't think that what you wrote is what you actually meant, a circuit requires a least 2 conductor.
 
9You say a motor requires 2 conductors( that would be 208v. But if it's a case like this 120v it would only require one conductor, a hot??
No, a 120v load only requires one "line" (ungrounded, i.e., hot, from a breaker) conductor, but still requires two wires to form a complete circuit.

No load can function when supplied by only a single conductor; current requires a circuit, so (at least) two wires are needed. Look at a lamp cord.

Don't confuse an EGC (grounding conductor) and a neutral (grounded conductor). You cannot use the EGC as a current-carrying circuit conductor.

A load does not care whether one of its supply conductors is grounded, only that the voltage between (or among) them is suitable for the load.
 
No, a 120v load only requires one "line" (ungrounded, i.e., hot, from a breaker) conductor, but still requires two wires to form a complete circuit.

No load can function when supplied by only a single conductor; current requires a circuit, so (at least) two wires are needed. Look at a lamp cord.

Don't confuse an EGC (grounding conductor) and a neutral (grounded conductor). You cannot use the EGC as a current-carrying circuit conductor.

A load does not care whether one of its supply conductors is grounded, only that the voltage between (or among) them is suitable for the load.

Then we have SWER!
 
No, a 120v load only requires one "line" (ungrounded, i.e., hot, from a breaker) conductor, but still requires two wires to form a complete circuit.

No load can function when supplied by only a single conductor; current requires a circuit, so (at least) two wires are needed. Look at a lamp cord.

Don't confuse an EGC (grounding conductor) and a neutral (grounded conductor). You cannot use the EGC as a current-carrying circuit conductor.

A load does not care whether one of its supply conductors is grounded, only that the voltage between (or among) them is suitable for the load.
Yes I thought so..lol. So even though it doesn't require a neutral and it's a 120v circuit 1 phase your still pulling a neutral as the 2nd conductor?
 
Yes I thought so..lol. So even though it doesn't require a neutral and it's a 120v circuit 1 phase your still pulling a neutral as the 2nd conductor?
Exactamundo. It doesn't require that either conductor be grounded, but it requires two conductors.

The fact that one conductor happens to be grounded is merely a characteristic of the source.
 