Attached is pic of panel schedule and unit schedule for these two units. It's a 3P4W panel, not sure why that would matter.
It's a pump that's being feed. So according to the schedule it's just one phase conductor but I would certainly pull a separate ground for a unit like this. My question is how does one determine if a neutral would be needed? I know a lot of motors don't need a neutral.
 

Attachments

  • Capture 1.JPG
    Capture 1.JPG
    45.2 KB · Views: 15
  • Capture.JPG
    Capture.JPG
    201.7 KB · Views: 15

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
My question is how does one determine if a neutral would be needed? I know a lot of motors don't need a neutral.
No motor requires a neutral (grounded conductor) per se, but does require two conductors (3 for 3ph).

A motor rated at 115v will receive one because our 120v supplies almost always happen to include one.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
No motor requires a neutral (grounded conductor) per se, but does require two conductors (3 for 3ph).

A motor rated at 115v will receive one because our 120v supplies almost always happen to include one.
You say a motor requires 2 conductors( that would be 208v. But if it's a case like this 120v it would only require one conductor, a hot??
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
On a 208/120V system.

A motor rated 115v will receive one _neutral_. Two conductors, a hot and a neutral. The 115V rating implies single phase, and the system implies a hot and a neutral.

A single phase 208V motor will receive two hots, but no neutral.

A three phase 208V motor will receive three hots, but no neutral.

-Jon
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You say a motor requires 2 conductors( that would be 208v. But if it's a case like this 120v it would only require one conductor, a hot??
I don't think that what you wrote is what you actually meant, a circuit requires a least 2 conductor.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
9You say a motor requires 2 conductors( that would be 208v. But if it's a case like this 120v it would only require one conductor, a hot??
No, a 120v load only requires one "line" (ungrounded, i.e., hot, from a breaker) conductor, but still requires two wires to form a complete circuit.

No load can function when supplied by only a single conductor; current requires a circuit, so (at least) two wires are needed. Look at a lamp cord.

Don't confuse an EGC (grounding conductor) and a neutral (grounded conductor). You cannot use the EGC as a current-carrying circuit conductor.

A load does not care whether one of its supply conductors is grounded, only that the voltage between (or among) them is suitable for the load.
 

retirede

Senior Member
Location
Illinois
No, a 120v load only requires one "line" (ungrounded, i.e., hot, from a breaker) conductor, but still requires two wires to form a complete circuit.

No load can function when supplied by only a single conductor; current requires a circuit, so (at least) two wires are needed. Look at a lamp cord.

Don't confuse an EGC (grounding conductor) and a neutral (grounded conductor). You cannot use the EGC as a current-carrying circuit conductor.

A load does not care whether one of its supply conductors is grounded, only that the voltage between (or among) them is suitable for the load.

Then we have SWER!
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
No, a 120v load only requires one "line" (ungrounded, i.e., hot, from a breaker) conductor, but still requires two wires to form a complete circuit.

No load can function when supplied by only a single conductor; current requires a circuit, so (at least) two wires are needed. Look at a lamp cord.

Don't confuse an EGC (grounding conductor) and a neutral (grounded conductor). You cannot use the EGC as a current-carrying circuit conductor.

A load does not care whether one of its supply conductors is grounded, only that the voltage between (or among) them is suitable for the load.
Yes I thought so..lol. So even though it doesn't require a neutral and it's a 120v circuit 1 phase your still pulling a neutral as the 2nd conductor?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Yes I thought so..lol. So even though it doesn't require a neutral and it's a 120v circuit 1 phase your still pulling a neutral as the 2nd conductor?
Exactamundo. It doesn't require that either conductor be grounded, but it requires two conductors.

The fact that one conductor happens to be grounded is merely a characteristic of the source.
 