The NEC is not crystal clear (on anything) yet it gives clear guidlines on this subject in Article 250. In section 250.30 the grounding of a separately derived system is explained. Keep in mind that the requirements of 250.4 must always be met also. in 250.30(A)(8)gives the rules for where a grounded conductor is installed and system bonding jumper is not installed at the source. In simple terms, an effective ground fault current path must be established, and if the system bonding jumper is installed at the disconnect then the grounded conductor must be at the disconnect because it is the return path for fault current to the source. If the system bonding jumper is installed at the source, then the equipment grounding conductor run with the circuit from the source to the disconnect is the return path for fault current to the souce, and therefore if no load is present for the grounded conductor there is no need for it to be installed.
In conclusion, if you ground and bond at the source(bonding and grounding must be done at the same place) then an equipment grounding conductor must be run with the conductors from that point, and if you ground and bond at any other point as allowed by 250.30(A)(1) then the grounded conductor must be run with the conductors to the point of bonding. Hope this helps, and read it slowly!
Fred Bender