In the example page 378/379 of MH 2005 Exam Prep, a maximum unbalanced load of 200A comes out to 2/0 cu neutral per 310.15(B(6). No problem there.
The example then goes on to say "in addition, 250.24(C) requires the neutral to be sized no smaller than 2/0 based on the 4/0 service conductors in accordance with Table 250.66
I don't see how 250.66 specifies this.
[ October 31, 2005, 12:19 PM: Message edited by: TimWA ]
The example then goes on to say "in addition, 250.24(C) requires the neutral to be sized no smaller than 2/0 based on the 4/0 service conductors in accordance with Table 250.66
I don't see how 250.66 specifies this.
[ October 31, 2005, 12:19 PM: Message edited by: TimWA ]