NEUTRAL QUESTION

Status
Not open for further replies.

hawkeye23

Senior Member
Location
stanton
I came across two mcc with a main circuit breaker each and a tie breaker between them which has a circuit breaker that supplies a 480v/277v panel for lighting. This lighting panel has two neutral conductors connected to it and can not trace both because of over wiring fill which can become dangerous tugging on wires. Is there a need for two neutrals?
Neutral and phase are the same size conductors . Also there is a 3 position switch for this panel.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So there are two neutrals in the panel feeder? Are they parallel neutrals? A 200% neutral for a lighting panel that had a large amount of non-linear loads wouldn't be out of the ordinary.
 

WIMaster

Senior Member
Location
Wisconsin
So there are two neutrals in the panel feeder? Are they parallel neutrals? A 200% neutral for a lighting panel that had a large amount of non-linear loads wouldn't be out of the ordinary.

+1
I worked on a bunch of places that specified 200% neutrals for harmonics.
 