We are serving a 3-phase, 4-wire load from a 3-pole disconnect switch without a solid neutral. Is it permissible for the neutral to go straight through the disconnect to the load? Or does it need to be terminated on a neutral lug in the switch?
No. This is a local disconnect for the piece of equipment served from a branch circuit panel in the building. Well down stream from the service entrance.
Service yes, feeder no.
I would look at 404.2B
Handy for troubleshooting, but I see no requirement in the NEC that it appear on a terminal.Thank you. Yes I know that the neutral should not be disconnected. My question is whether or not it is required to be terminated on an insulated neutral lug in the disconnect or can it go straight through the disconnect to the load?
My question is whether or not it is required to be terminated on an insulated neutral lug in the disconnect or can it go straight through the disconnect to the load?
It can pass straight through, there is no reason and no code rule to land it if you do not want to.
I would pass through assuming it was easy.
Would doing that make the disconnect enclosure a pull box and subject to the associated sizing and conduit spacing requirements which might not be met?