Building with 120/208V service has one load that needs 480V and that does not need a neutral. Plan is to use step-up 208-480 transformer, with an enclosed circuit breaker (ECB) feeding directly to the load. I am thinking that I need to connect a GEC to the secondary center point. I would call for the N-G bond at the transformer. I believe that I need not bring a neutral to the ECB or to the load itself.
Comments?
That's fine, done all the time really if you think about an MCC that has no loads requiring neutral, but is fed from a 480Y277 service. The service gets bonded, but no need to put the N bus in the MCC, so no need to run the N conductor out to it.
My only suggestion (based on experience) is to not assume the installer understands that the "secondary" in this case is the 480V side, so refer to it as the HV and LV sides of the transformer. Also make sure that they know that they need to use a transformer with a
wye on the 480 side and not to bond the X) on the 208V side (if there is one). Common off-the-shelf distribution transformers are mostly 480 delta, 208 wye. It's not hard to find a 480V wye version, it's just not something they will pick up out of a distributor's stock.
Edit:
Or use a delta on the 480 side and corner ground it. Not a good plan if there are power electronics, but it sounds as if that's not the case here.