I have a 480V Siemens P5 Panelboard with 1200A 3P-LNX Main Breaker with a 555 ETU-LSIG, GF Trip with a neutral sensor (CT).
This panel is currently fed from a from a 13.2 - 480V Xfmr. We are now eliminating the transformer and bringing in a direct 480V feed to this panel from one of the MCCs. I want to know if not wiring the neutral thereby not using the neutral CT in the panelboard will be okay. Will there be something that I need to change in the 555-trip unit to disable the GF trip? The panelboard has three 3P-LMX breakers that feeds rental units.
This panel is currently fed from a from a 13.2 - 480V Xfmr. We are now eliminating the transformer and bringing in a direct 480V feed to this panel from one of the MCCs. I want to know if not wiring the neutral thereby not using the neutral CT in the panelboard will be okay. Will there be something that I need to change in the 555-trip unit to disable the GF trip? The panelboard has three 3P-LMX breakers that feeds rental units.