We have six parallel runs of 750MCM aluminum USE conductors per phase, going between the utility transformer and an open bottom 2000A outdoor service disconnect.
My question is, how many neutrals (grounded conductors) do I need to run in that trench?
Using the 12 1/2% rule from table 250.102(c)(1) it would require roughly 600MCM.
250.24(C)(2) talks about parallel conductors in two or more raceways or cables, but no mention of direct bury installations.
I understand that if it was in conduit, each raceway would require 600MCM, but can't find anything that addresses this issue in a trench.
Thanks in advance!